Hi, in your screenshot, only the "CONNECT" parameters are shown. These are used for connection handling itself, but this does not read/write anything. You have to use correct value for parameter "MB_MODE" to select which modbus function (read, write) should be processed. With the other block parameters you can decide which addresses should be read/written. But "where" (address/register) the values for "voltage, energy, ...)" are provided by the modbus server, should be described in it's manual. Description of MB_CLIENTMB_MODE, MB_DATA_ADDR and MB_DATA_LEN parametersregards sancruz |