Hi . I dont know if Im so late but i need your Help . Im in windows10 , step7ver5.7 wincc2008 ..... I have projet created with PACKNGO wih other PC FOR TP 1200 CONFORT and i try to transfert it to tp1200 but no possible to establish connection with PC . what can be a problem and i want to know if i need other software ? i have prosave ver 14 . thanks ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/02/2023 09:12:07New subject after splitting |
|
3/10/2023 1:50 PM | |
Joined: 8/3/2009 Last visit: 11/8/2024 Posts: 14127 Rating: (1769)
|
Hello byahya A Comfot Panel can only be programmed with TIA Portal not with WinCC flexible 2008!!! there are also requirements for Pack and Go: If you are using TIA Portal then have allok at the Pack and Go manual here in this FAQ: https://support.industry.siemens.com/cs/de/en/view/109476153 Bye Murof |