Joined: 5/15/2023 Last visit: 5/28/2023 Posts: 3 Rating: (0) |
Hi Friend, Im Looking conect the LOGO with Fronius inverter, can you give me some advise to do it please? I dont have idea how to start. Best Regards!
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 05/16/2023 10:28:37New subject after splitting |
|
5/16/2023 4:42 AM | |
Joined: 12/18/2014 Last visit: 9/20/2024 Posts: 33807 Rating: (4200)
|
Maybe this topic in the German-speaking part of the Forum will help you ... Daten aus Fronius GEN 24 mit Logo 8.3 auslesen |
5/28/2023 2:43 AM | |
Joined: 12/18/2014 Last visit: 9/20/2024 Posts: 33807 Rating: (4200)
|
Your first problem is the overlapping of the addresses in the VM memory. The normal analog network input (NAI) is designed for reading INT16 (range -32,768 to 32,767), not for UINT16 (range 0 to 65,535). Is the value greater 32,767 then the LOGO! interprets this as a negative number. AttachmentLOGO! Bit, Byte, Word and DWord.pdf (463 Downloads) |
Last edited by: ixo65 at: 05/28/2023 02:50:23Last edited by: ixo65 at: 05/28/2023 02:50:39 |
|