Hi Everyone, As I know we can use ET200SP HA Redundant IM in PCS7. Can we configure ET200SP HA Redundant IM with PLC S7-400H (i.e. CPU 412-5H, 414-5H etc.) with WinCC & STEP7 (SIMATIC Manager). Please refer attached system architecture; kindly suggest if any chnages. Regards, Arun Jadhav AttachmentET200SP HA IM in Redundant configuration with S7400H.pdf (888 Downloads) |
5/30/2023 6:00 AM | |
Joined: 10/7/2005 Last visit: 9/22/2024 Posts: 3021 Rating: (1054)
|
Yes you can use the ET200SP HA with an S7-400H (FW 6 or later CPU's) and Step 7 (V5.6 or later) is the short answer and THIS FAQ has more details. |