Hello, when you configure the TO and download like described in the manual, the configuration data are stored permanent. 5. Positioning axis technology object https://support.industry.siemens.com/cs/ww/en/view/109773400 TO of S7-1200 supports no position tracking. S7-1500 has the functionality. When absolute encoder has an overflow, TO takes the wrong position from the drive, after power Off/On, because TO counts no overflow of the absolute encoder. |