11/22/2016 2:06 PM | |
Joined: 9/27/2006 Last visit: 11/4/2024 Posts: 12293 Rating: (2690) |
Hello Iftekar; You seem to be on the right track: SFC12 Mode 2 will deactivate the slave designated by its Logical Address (LADDR); we usually use the diagnostic address of the module, provided by HWConfig. You can use any available bit address for the REQ and BUSY signals, but you should look at the following documents, FAQs from Siemens and an extract from a Hans Berger book (found on the web, if you want to consult it), that indicate how your program must use these bits to control the operation of SFC12 over more than one scan (it is an asynchronous function_: Notes for the use of the system function SFC12 "D_ACT_DP" https://support.industry.siemens.com/cs/fr/en/view/17624225 Enabling a disabled DP slave with SFC 12 'D_ACT_DP' https://support.industry.siemens.com/cs/fr/en/view/19730984 Hope this helps, Daniel Chartier |
This contribution was helpful to2 thankful Users |
11/22/2016 4:59 PM | |
Joined: 1/21/2013 Last visit: 10/23/2024 Posts: 4620 Rating: (708) |
Hello, other infos for SFC12: |
11/23/2016 5:51 PM | |
Joined: 1/21/2013 Last visit: 10/23/2024 Posts: 4620 Rating: (708) |
again CTRL + ALT + Q no help? It's possible that you have the same "problem", look below: Address of Profibus |