Hello, in my opinion you have a wrong parameterization of your analog input module. You have your measuring range set to 0..20 mA. You must parameterize your measuring range for the module to 4..20 mA. Please have a look at the manual SIMATIC ET 200SP analog input module AI 8xI 2-/4-wire BA At page 34 you can see with values your IW must have at which current. regards |
11/25/2024 12:57 PM | |
Joined: 8/6/2018 Last visit: 12/19/2024 Posts: 322 Rating: (42) |
Hello, have you tried increasing the smoothing? Smoothing Produces a stable analog signal. Thanks you |