Hello, Somebody knows?, How comunicating aS7-300 withto RTU Kingfisher?, The protocol of comunication is by serial MODBUS, if somebody knows something or has an example please sendme to my e_mail: e_e_c_c@hotmail.com, thanks. |
9/12/2006 9:37 AM | |
Joined: 9/28/2005 Last visit: 12/14/2022 Posts: 414 Rating: (28) |
Hi, The only waycommunication via Modbus for Siemens S7-series is Modbus RTU. The S7-300 can act as Modbus RTU slave or as Modbus RTU master, therefore you need an extra driver (which is also a plugin module) for the CP341. See for more information and downloads: http://support.automation.siemens.com/WW/view/en/18248289 http://support.automation.siemens.com/WW/view/en/22637279 |
Smurf |
|
9/24/2006 10:58 PM | |
Joined: 1/7/2006 Last visit: 11/17/2023 Posts: 2705 Rating: (318)
|
[quote user="E_CHENA"]How comunicating aS7-300 withto RTU Kingfisher?, The protocol of comunication is by serial MODBUS, if somebody knows something or has an example please sendme to my e_mail: e_e_c_c@hotmail.com, Hi Mr. Chena, Please look to the thread Modbus Network where I have spoken over a Modbus Master, but the links for the slaves are also in there. It is not difficult, when you place the example in the CPU it will works. The only thing you have to search for are the FUNCTION CODES that are used from the RTU Kingfisher, those FC are programmed in the Hardware Projecting of STEP7 after you have installed the Modbus Slave driver and of course the serial cards programming. So you have to determine which FC are to programmed into the CP341. |