Industry Online Support
Technical Forum
1/24/2012 8:53 PM | |
Posts: 311 Rating: (3) |
Hello all, I have this sensor: http://www.kimo.se/pdf/FT_TB50.pdf(TB50 A 3 S 6 50 12 G), how should I connect this to the analog input ob the 1200 PLC ? The picture show the inside. Thanks Per Olof |
1/24/2012 9:19 PM | |
Posts: 6 Rating: (0) |
Hello, I often use something like this: https://eshop.phoenixcontact.com.sg/phoenix/treeViewClick.do?UID=2864435&parentUID=852472389&reloadFrame=true to convert the PT100 signal to a 0-10V / 4-20mA signal Grtz |
1/24/2012 9:54 PM | |
Posts: 20 Rating: (1) |
U must use RTD module. Look this: /tf/WW/en/Posts/67845 Second option is a convert PT signal to 0-10/4-20 signal. |
Follow us on