I have a program at a PLC and it writes a value of 2to a DB DB197.DBD0 when i take a look to the variable table i can see the value is 0 instead of 2 i have checked where this value has been added 1. i took a look to direct asignment with move 2. also checked SFC20 calls and none of this is affecting i dont have ideas where it is taking this 0 value any ideas? regards, AttachmentPrueba09062012_V2.zip (39 Downloads) |
6/10/2012 6:42 AM | |
Joined: 1/28/2009 Last visit: 8/5/2024 Posts: 6844 Rating: (1365) |
Hello , As shown in the attachmnet you have written in the same address 13 times (check it by "go to location" capability in LAD/STL/FBD editor).In some cases they are constant and some of them are variables. I suggest to check all cases to see in which case the address written by zero! Also check this: indirect adress tracineHope this helps Best regards, Hamid Hosseini AttachmentDB197.zip (32 Downloads) |