8/4/2014 12:12 PM | |
Posts: 1368 Rating: (126) |
No, i do not open it... What status value you get while TSEND_C is active (note: copy the value in memory in case of an error!). |
8/5/2014 10:35 AM | |
Joined: 9/1/2005 Last visit: 11/5/2024 Posts: 4109 Rating: (195) |
new question published by minoanis split to a seperate thread with the subject Simulate the network connection between two PLC by PLCSIM V13. Best regards CS Moderator |
My Forum is the place to personalize your profile, |
|
8/18/2014 7:19 AM | |
Posts: 146 Rating: (0) |
....Maybe i disturbed mamy times.. Please help me..till now I couldn't connect two PLC S7 1200... I just want ..when I press I0.4 form PLC 1 (CPU 1214C) then Q0.0 PLC 2 (CPU 1215C) will "ON". I attach my file ...Please check for me to communicate between two PLC.... ( When you downloaded..please change from Test.zip ---> Test.rar and open my example). Thank you very much ! Besr regard ! AttachmentTest.zip (218 Downloads) |
8/18/2014 10:14 AM | |
Posts: 1368 Rating: (126) |
Hello, do you implement my advices and tips from the posts before? |
8/18/2014 12:31 PM | |
Posts: 1368 Rating: (126) |
Hello, it is not allowed to use a single BOOL on parameter DATA of TSEND_C. You must use a byte minimum...e.g. IB0 |
8/19/2014 10:50 AM | |
Posts: 1368 Rating: (126) |
Hello, in network 4 (OB 1) of PLC 1 you overwrite your IB0 with QB0. Why? So I0.4 will not be true any more... Delete this network. Just Move IB0 -> MB10. |