Dear sir, I have an Simoreg make DC drive with model no 6RA24, I ma getting error F005 fault code. I checked P047 parameer, it shows 4. What I next to check ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 8/24/2018 11:28:52 AMNew subject after splitting |
|
8/24/2018 10:04 AM | |
Joined: 8/25/2006 Last visit: 11/1/2024 Posts: 2210 Rating: (279)
|
Hello. Links to the manual were given in this post. P047=4 means: Voltage failure or Ifield_act<50% Ifield_set longer than that set at parameter P086 (if this >0). |
8/25/2018 2:06 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, Please check the field circuit side AC fuse link. Also please check the field winding resistance & field current. If the problem persist, please provide motor nameplate details. If you had provided motor nameplate details, it would have been much easier for forum mebers to help you much better. |