Joined: 1/4/2007 Last visit: 11/13/2024 Posts: 1147 Rating: (175)
|
Hello Urantia, If you change the load cells, you have to do a new calibration. For a calibration, you have to do: 1. go online with Siwatool 2. receive all data 3. follow the instructions of the chapter 6 of the attached file. Best regards Siwarexi AttachmentSIWAREX_FTA_Quick Guide_SIWATOOL_V2_05.pdf (219 Downloads) |