Hi everyone I got big problems I have a 6ra24 Drive and it faults when attempting to run the second phase of Auto Tune (P51=26). Drive begins to ramp up and in a few seconds shuts down with error code F042 Tachometer Fault. Needs some troubleshooting ideas, as far I know the tach is wired and okay the best we can tell. The only thing I can think of at this moment is the shield is not grounded at the drive unit yet. Just hit me as I am sending this out. Thanks Everyone! AttachmentSIMOREG 6RA24_ATC.zip (687 Downloads) |
1/6/2020 4:30 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, You should have post this in DC converters SIMOREG product conference. P=026 - speed controller optimisation run - Are you conduting it with motor connected to load or at no load condition. Check if it works at motor no load condition. How you have checked tacho output? Is tacho DC voltage output is stable or fluctuating? Check the value in P200, increase it & check if the problem gets solved. If yes, your tacho output is in more in pulsating form & you need to replace it. HTH
|
This contribution was helpful to1 thankful Users |
1/6/2020 3:21 PM | |
Posts: 3 Rating: (0) |
Thanks PISCEAN 2010 We have only run this with the load coupled to the motor. Which this is a huge flywheel on a 400 Ton press application. We will try and tune the motor tomorrow with the belts disconnected from the motor and I will let you know how it goes. I also posted my program attached below that I recorded with drive monitor for review. Sorry for the wrong post, it was my first online post so I am a newbie. Have a good day!
AttachmentSIMOREG 6RA24_ATC.zip (654 Downloads) |
Last edited by: AutoGen_818657 at: 01/05/2020 15:23:16Last edited by: AutoGen_818657 at: 01/05/2020 15:26:28 |
|
1/7/2020 4:47 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Have you tried to optimise motor without load as stated in this post?. |