5/23/2014 8:18 PM | |
Posts: 4 Rating: (0) |
Hi Guys. I got a Siemens Logo 6ED1 053-1HB00-0BA2 PLCand when I upload a small latter program it works fine. But when I add a little more it comes with an error: 0BA2.L Transfer not possible, because the connected LOGO! is incompatible. Refer to the device selection dialog to determine which devices you can use for this program. 0BA2.L:B005/2Input inversion not supported Download PC --> LOGO! failed This small test circuit is uploading fine: [....] This expanded circuit can't upload:[....] The expanded circuit is working in the Logo Comfort when I use F3 "preview" so it's now because I've made a mistake in the circuit. (I have also tried other Circuits that I have uploaded on other Logo's with no problems) When i press F12: The following LOGO! can be used: 0BA1.Standard 0BA1.L 0BA1.LB11 0BA2.Standard (I guess this is mine??) 0BA2.Standard Analog 0BA2.L 0BA2.LB11 0BA3.Standard 0BA4.Standard 0BA5.Standard 0BA6.Standard 0BA6.ES3 I hope you guys can help. Thank you. Attachmentatt.zip (269 Downloads) |
Last edited by: GrasserF at: 5/26/2014 7:39 AMlinks deleted, insert attachment |
|
5/23/2014 11:15 PM | |
Joined: 12/27/2006 Last visit: 8/18/2024 Posts: 1197 Rating: (113) |
Have you set your LOGO!Soft programm for the rigt LOGO! Use CTRL+H and choice for 0BA2 |
5/24/2014 1:06 AM | |
Posts: 98 Rating: (6) |
Hi, Your Firmware LOGO! does not support the fuction that you see on the error "B005..." In the next Link you can see, points 6 and 7, almost at the end on the error part. https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&lang=es&objid=21961314&caller=view
|
Last edited by: GrasserF at: 5/26/2014 7:43 AM |
|