Hello Kiiza; Whenever you test a program using PLCSim, you must always keep in mind that you are using a simulated CPU, there are functional differences between the simulation and real hardware. Here is a FAQ that discusses these differences. Amongst other points it states that PLCSim does not handle time values as in a real PLC, which could explain your results: https://support.industry.siemens.com/cs/us/en/view/11610958 Hope this helps, |