5/9/2018 9:46 AM | |
Joined: 3/14/2008 Last visit: 10/8/2024 Posts: 2109 Rating: (941)
|
Kargan, Try setting I/O: "ACC_MODE" to "1" and back to "0" again on the module in your screenshot Check again. Do you have your CPU setup so that Cold restart is possible? And was a cold restart initiated? If so, make sure this does not happen again! cold restart is not released for PCS7, you should disable it in hardware configuration (requires stop). |
Last edited by: Oreca at: 5/9/2018 9:49:09 AMLast edited by: Oreca at: 5/9/2018 9:49:36 AMIf I could help you, you can use the RATE button. Thank you. |
|
5/15/2018 2:21 PM | |
Joined: 6/19/2008 Last visit: 8/6/2024 Posts: 46 Rating: (4) |
OK case closed ;) Once again - its very important to read Software requirements and NEVER trust that somebody did his job - just check by yourself :D So for your info: AddFEM Library V8.2 requires PCS7 Basic Library V8.2 Upd2 (or higher) https://support.industry.siemens.com/cs/pl/en/view/109744892 We are using customer ES station with Basic Library V8.2 Upd3 but... customer didn't update his Master Library which contained the old blocks (among others important FB118 OB_DIAG1). Because of old blocks in master Library also AS offline folder contained old blocks... That was a reason why AddFEM had a problem with AS redundancy. BR Kargan |
Last edited by: Jen_Moderator at: 5/16/2018 8:23:57 AMOptimized link. |
|
This contribution was helpful to1 thankful Users |