Hi dear H_H Thanks for your informative post.Please check the attachment in which 2 DO are connected via 2 diodes to a relay.Is it possible to implement such configuration with SIEMENS modules or external diodes should be bought? Best regards hdhosseini Splitted from Isolated Channel for DO. Attachmentred_out.zip (234 Downloads) |
Last edited by: O_Moderator at: 10/4/2010 1:20 PMnew subject after splitting |
|
10/3/2010 12:49 PM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (309)
|
Hello hdhosseini, Siemens has some digital output modules with internal diodes for parallel operation. The attached PDF has been extracted from S7-400H manual. You can also find which modules have internal diodes when you look at the detailed specification in S7-300 module data. Best regards. H-H AttachmentRED-DQ.pdf (286 Downloads) |