Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181) |
Parallel connection of same type of power supplies for redundant operation More info at http://support.automation.siemens.com/WW/view/en/18123560 |
2/18/2013 6:42 AM | |
Posts: 7 Rating: (0) |
HiUMENCHO, Thanks for your reply. However, my question is not on the wiring or the whole setup itself, but rather the switch setting on the power supply. Should i use parellel operation at Switch A or single operation at Switch A. Refer document:BA_6EP1437-3BA10_7
AttachmentBA_6EP1437-3BA10_7.pdf (607 Downloads) |
2/18/2013 12:37 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715) |
Hello, This switch is used when you put 2 Sitop in paralel to increase performance. The output voltage regulation will be affected. For redundancy you need a powersupply that can power the installation by itself, the second supply is just in case 1 powersupply breaks, therefore diodes or a module is needed. Secure 24 V DC even when a power supply unit fails Regards, Marcjan |
Problem solved? |
|
2/19/2013 6:57 AM | |
Posts: 7 Rating: (0) |
HiMarcjan/UMENCHO, Thanks your explanation. I think i'm clear on the issue. Best Regards, Josh Cheang
|
This contribution was helpful to1 thankful Users |
1/15/2016 10:24 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
New question published by vikas soni is split to a separate thread with the subject Redundancy of two Siemens SITOP. Best regards |