I have a CPU 1212F v15.1 with safety program, I am getting an error "the consistent fail-safe upload is not enabled for this online device. either the online device doesn't support fail-safe upload or the appropriate setting in the safety administration editor is not active and downloaded" What I am missing or is not possible? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/02/2021 05:44:48New subject after splitting |
|
3/2/2021 10:02 AM | |
Joined: 3/11/2019 Last visit: 11/8/2024 Posts: 1653 Rating: (304) |
Dear OscarOlivasRosas, the setting "the consistent fail-safe upload" is only possible for CPU-1500 with firmare V2.1 or newer.. This parameter has to be set *before* the initial download to the CPU. IF the program on the cpu was downloaded without this setting, an upload is not possible. For CPU-1200, this option is not available at all, means, an upload of safety program from a CPU-1200 is not possible in general. Informations can be found here (also for V15/V15.1): SIMATIC STEP 7 Basic/Professional V16 and SIMATIC WinCC V16"The consistent hardware and software upload enables a loading of project data (including safety-related project data) from a fail-safe S7-1500 CPU*) to a programming device / PC. The project data are loaded without an additional generation step and are consistently available in the TIA Portal for immediate continued work. *) As of firmware version V2.1 "regards sancurz |