Mike boa tarde. Após habilitar a proteção de sub e sobre tensão no relé 7sj8041. Led 1 entrou em trip e não consigo mais efetuar configuração devido a uma falha esta ativa. Pode ajudar nessa questão?
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 01/24/2022 12:13:47New subject after splitting |
|
1/22/2022 7:16 PM | |
Joined: 12/18/2014 Last visit: 1/21/2025 Posts: 34530 Rating: (4307) |
Hello Naldo Cardoso, at first welcome to the forum. This is a english speaking forum. Please be so kind and write your next posts in english.
|
This contribution was helpful to1 thankful Users |
2/10/2023 12:28 PM | |
Joined: 10/9/2007 Last visit: 1/17/2025 Posts: 1253 Rating: (115)
|
Hi voltage protection must be blocked in the absence of the current. Look for this parameter on the voltage protection setting |