Joined: 3/11/2019 Last visit: 8/7/2024 Posts: 1546 Rating: (277) |
Hi Bo-Anders, it is only possible with a CP 1543-1 firmware version V2.2 or higher (not CM), the CPU needs firmware V2.8 or higher and the projects needs to be at least TIA V16. Access to OPC UA applications
regards sancruz |
Feedback appreciated, please rate |
|
This contribution was helpful to3 thankful Users |
2/7/2022 1:58 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
hi Bo-Anders, normally everything you need to know about OPC UA with S7-1500/1200 PLCs can be found in this manual: What you need to know about OPC UA hope this helps, regards, |