Hello Ahmed; Your configuration seems to follow the standard "Open Ring" topology for S7-400H systems using Profinet. It is not exactly MRP, which involves the use of switches as ring managers/clients) but it is approved, as you can see in this document "Configuration Examples for S7-400H with PROFINET": https://support.industry.siemens.com/cs/ww/en/view/90885106 Daniel Chartier |
3/23/2022 10:54 AM | |
Joined: 2/23/2021 Last visit: 8/3/2024 Posts: 10 Rating: (0) |
I have connected the ports interconnection in the topology editor (Snapshot is attached) which represents the "Open ring" topology, Please confirm this step is correct and no further steps are required in Hardware configuration to configure "Open ring" topology. |
3/23/2022 11:13 AM | |
Joined: 2/23/2021 Last visit: 8/3/2024 Posts: 10 Rating: (0) |
Before I've mentioned that I have 5 IO devices connected to my H-Station, these IO devices are as follows:
2- ET200SP (with Interface module 6ES7155-6AU01-0CN0), (14 AO modules 6ES7135-6HD00-0BA1) & (22 DO modules 6ES7136-6DC00-0CA0) 3- three identical ET200M racks (with Interface module 6ES7153-4BA00-0XB0) & (10 AI modules 6ES7336-4GE00-0AB0) each. |