7/25/2017 5:15 PM | |
Posts: 5 Rating: (0) |
I have selected 6ED1055-1MA00-0BA2. I need to coneect 3 wire transmitter to this model. Please send me the connection diagram. |
7/25/2017 5:22 PM | |
Joined: 12/18/2014 Last visit: 6/8/2024 Posts: 33165 Rating: (4098)
|
We need more information. Does the tranmitter has its own voltage supply or the same as the analog expansion module? What is the signal from the transmitter? 0-10V or 0/4-20mA? AttachmentLOGO! 8 Soft manual 0BA8 2016_07 (FS4) page 49.pdf (976 Downloads) |
Last edited by: ixo65 at: 7/25/2017 5:28:22 PMAttachment |
|
This contribution was helpful to1 thankful Users |
7/25/2017 5:31 PM | |
Posts: 5 Rating: (0) |
Dear sir Thanks for the quick response. We have used Honeywell Gas detector , I am attaching the wiring detail for Honeywell Detector. Please refer figure 37 in the attached file. Where i need to connect on Analog Module 6ED1055-1MA00-0BA2 Regards Harsh AttachmentHoneywell Gas detector.pdf (461 Downloads) |
7/25/2017 6:01 PM | |
Joined: 12/18/2014 Last visit: 6/8/2024 Posts: 33165 Rating: (4098)
|
Try it so. |
This contribution was helpful to2 thankful Users |
3/19/2020 6:56 AM | |
Joined: 3/19/2020 Last visit: 10/18/2023 Posts: 1 Rating: (0) |
Thank You! |