4/1/2012 3:53 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, Have a look to this example: http://support.automation.siemens.com/WW/view/en/6518822 Its a S7-300 as I-Slave of a S7-400. Comparable with your setup where the IM151-7 is an i-Slave of a S7-313 The fact that you do not have a BF on your S7-313 (but on the IM151 you have BF) indicates clearly that the 313 does not have any slave configured in its HW. Basic procedure is 1) to have the 313C and the IM151-7 in the same project. 2) To access the slave for programming over the bus, check the box "test, commisioning, routing" as in the picture in annex. 3) Add the i-Slave IM151-7 in the HW of the 313 as "Configured station ==> ET200S CPU). Couple the IM151-7 in the same project to the 313 and start to configure the areas that the IM151-7 and the 313C will exchange. 4) download slave and master. |
Best regards |
|