5/11/2022 6:31 PM | |
Joined: 11/8/2017 Last visit: 6/2/2024 Posts: 324 Rating: (176)
|
Hi, I'm not familiar with the type of Fire system you refer to, but for your first point - you should try using Reactions and Macros within CC. Create a Reaction to detect the alarm-points going to a specific state, then create a Macro to command the relevant DXR points to disable the FCUs. The last part is to add the Macro into the Reaction - so that when your conditions in the Reaction are met, the Macro is executed by the Reaction. You will also need to create the same setup to release any commands/overrides that you apply to the DXR, i.e. when the fire alarm point goes back to Normal, the FCU points are released back to an auto state. In summary, you would need a reaction and a macro to disable the FCUs, and another reaction and macro to put the FCUs back to normal operating mode. For your second point - this was discussed HERE. It may be the case that you need to manually configure alarms within CC for each of your integrated points. Regards, |