6/29/2019 8:58 PM | |
Joined: 5/6/2010 Last visit: 9/21/2024 Posts: 1978 Rating: (276) |
Hello Jay, are the sensors from E+H types that could configured? regards |
6/30/2019 3:03 AM | |
Posts: 1283 Rating: (105) |
Hi CaOd, these sensors are preconfigured already. |
6/30/2019 10:09 AM | |
Joined: 5/6/2010 Last visit: 9/21/2024 Posts: 1978 Rating: (276) |
Hello Jay, could be there a problem with the power supply of your modules? regards |
6/30/2019 1:47 PM | |
Posts: 1283 Rating: (105) |
I will check with it. I am using PM1207 for the power supply for all modules and also for the flow meter. I will check the power supply cables |
7/1/2019 4:44 PM | |
Joined: 9/19/2011 Last visit: 9/13/2024 Posts: 140 Rating: (33) |
Hello Jay, I believe that you have the correct wiring, but I just wanted to be sure. It is important that the 24V power supply return (M) be connected correctly. Attached is the correct wiring for three 2-wire sensors. Larry Attachment2-wire 3-sensor connections.pdf (194 Downloads) |
This contribution was helpful to1 thankful Users |