1/9/2017 7:14 AM | |
Posts: 3 Rating: (0) |
Good afternoon, When using the CPU 416-3 DP (6ES7 416-3XR05-0AB0) controller we had a not foreseen in the Stop mode. Analysis of the diagnostic buffer contents revealed no software failures, the controller simply moved to the stop, both with a manual switch. Could you advice for a given fault. We can not be sure operation of the controller on. The contents of the diagnostic buffer. Diagnostic buffer of module CPU 416-3 DP Order No./ Description Component Version 6ES7 416-3XR05-0AB0 Hardware 4 - - - Firmware V 5.3.1 Boot Loader Firmware expansion V 5.3.0 Rack: 0 Slot: 3 Serial number: SVPXD167156 Settings: Time including CPU/local time difference (0 h) Event 6 of 120: Event ID 16# 530D New startup information in STOP mode Startup prevented by: - STOP request exists - Keyswitch set to STOP - Cold restart or warm restart necessary Startup information: - Time for time stamp at the last backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted Last valid operation or setting of automatic startup type at power on: - No startup type/following memory reset Operating mode: STOP (internal) Incoming event 09:01:33.464 PM 01/01/2017 (Coding: 16# 530D FF04 C777 0061 0810 0700) Event 7 of 120: Event ID 16# 4303 STOP caused by stop switch being activated Previous operating mode: RUN Requested operating mode: STOP (internal) Incoming event 09:01:33.462 PM 01/01/2017 (Coding: 16# 4303 FF84 0000 0000 0000 0000) ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 1/9/2017 3:03:23 PMNew subject after splitting |
|
1/11/2017 6:09 AM | |
Posts: 3 Rating: (0) |
Thanks for the answer. This CPU malfunction after 01Jan2017 was replaced by a new one 05Jan2017. Although after a warm restart 01Jan2017 CPU 416-3 DP was working properly, and I think would work more smoothly indefinitely. Everything points to the switch. But at the moment of failure in humans indoors PLC was not (there signaling). The switch was in the RUN position and the LED displays STOP. Later transferred to probyvali stop remotely via Simatic Manager through Operating mode- stop formed at the stop with SFB20. We tested the CPU 416-3 DP on the lab bench. We try to do a reset via MRES. The switch works steadily (no chatter) on the vibration does not respond. As a result, we updated the firmware to v5.3.5 and left to test. While the controller is working properly. But the root cause of failure is not found . To understand the operation of the switch need functional block diagram of the controller.
Attachmentstop_cpu010117.ZIP (258 Downloads) |
Last edited by: Sald84 at: 1/11/2017 6:19:48 AM |
|
4/13/2018 8:34 AM | |
Posts: 7 Rating: (0) |
Hello friends, I have PCS sytem in my plant in which most of the CPU are 416-3,yesterday while downloading the program changes only CPU went to stop mode,i have attached the diagnostic buffer file,please suggest how can avoid this in future, Thanks AttachmentCPU 416-3 STOP MODE.pdf (322 Downloads) |