Starting or peak current of motor would be 486 A but it would not be same for 10 sec i.e. during accelration time. As motor starts acclerating the current starts droping. Please refer Current transformer for low voltage & 4NC5_en.pdf documents. The overcurrent limiting factor is expressed as FS & a factor, in this case it is FS5. So overload factor of CT is based on short circuit current & not on the inrush current of load. Please also refer Ith & Idyn values of CT in documents for more information. HTH. |