Hello Having an AI-Card (6ES7331-1KF01)config for 4-20mA. Have connected an PT100 with converter (0-100C->4-20mA) Feeds the PT100 with 24V+ and the value from PT100 to I+ (ch 2 (12)). Then M- to 0V (ch 2 (15)). The messuringvalue is aprox. 10C* higher than it should be, when i connect an simulator on the card it seems to be OK, there must be som kind of missmatch. the powerunit is grounded on the M-. Any idé??? Hej Har kopplat in en PT100 givare med omvandlare i huvudet 0-100->4-20mA. Problemet är att jag ligger cirka 10 grader över vad jag borde. Har kopplat +24V ut till givaren, svaret tillbaka in på I+ samt minus på M- (ch 2 Uttag 12 och 15). Simulerar jag direkt på kortet verkar det stämma linjärt, någon idé. |
Last edited by: NickeNyfiken at: 6/9/2010 4:45 PMLast edited by: NickeNyfiken at: 6/9/2010 4:38 PM |
|
This contribution was helpful to1 thankful Users |
6/9/2010 4:40 PM | |
Joined: 3/21/2006 Last visit: 1/14/2025 Posts: 10239 Rating: (1182) |
Hello, Please, could you translate in English language. Or perhaps someone elase could do this.
Best regards, Hristo Mihalev |
6/9/2010 4:41 PM | |
Joined: 7/16/2006 Last visit: 1/2/2024 Posts: 1502 Rating: (176) |
Hi Vær oppmerksom på at engelsk er et forum her. Har de spør henne hvorfor, selv i dette språket. Har de har denne forståelsen, siden de ikke solen kan bli hjulpet. Hej Bemærk venligst, at engelsk er et forum her. Har de spørger hende hvorfor, selv i dette sprog. Har de denne forståelse, da de ikke solen kan blive hjulpet. Gruss |
Karl |
|
6/9/2010 4:48 PM | |
Joined: 7/16/2006 Last visit: 1/2/2024 Posts: 1502 Rating: (176) |
Hi >The messuringvalue is aprox. 10C* higher than it should be, >when i connect an simulator on the card it seems to be OK, >there must be som kind of missmatch. the powerunit is grounded on the M-. >Any idé??? Perhaps a scaling problem. At first. Tell mit the temperatureon senor, what mA you have. As example: Sensor 20°C --> 3 mA Sensor 100°C --> 20 mA As example Tell us the value for20°C, 100°C Messuring with an external gauche. ( Digital current measurement) |
Karl |
|
This contribution was helpful to2 thankful Users |
6/10/2010 7:34 AM | |
Posts: 65 Rating: (1) |
Hi When simulate direct on the card (Pin 12 och 15) 4mA=0C* 20mA=100C* So no scaling problem. |
6/10/2010 4:57 PM | |
Joined: 7/16/2006 Last visit: 1/2/2024 Posts: 1502 Rating: (176) |
Hi >When simulate direct on the card (Pin 12 och 15) >4mA=0C* >20mA=100C* >So no scaling problem. O.K. conecting the PT100 --> conerter --> Pin 12, 15) Integrate only for test the "Digital current measurement". Put the Sensor in ICE-Water (0°C) --> How mA do you have (You must have 4 mA) Put the Sensor in hot Water (100°C) --> How mA do you have (You must have 20mA) As example If you have 0°C --> 0mA If you have 100°C --> 20mA You have a scaling problem. Test if you can change from 0-20mA to 4-20mA. (PT100 converter) Have you a Datasheet from your converter ? Type ? I think, this can solve you problem. |
Karl |
|
6/11/2010 9:40 AM | |
Posts: 65 Rating: (1) |
Hi It's an INOR PT100 calibrited 0-100C*-->4-20mA |
6/11/2010 7:00 PM | |
Joined: 7/16/2006 Last visit: 1/2/2024 Posts: 1502 Rating: (176) |
Hi Do you have make the test from my information (6/10/2010, 4:57 PM ) With this information can you test the converter. |
Karl |
|
6/11/2010 7:04 PM | |
Joined: 7/16/2006 Last visit: 1/2/2024 Posts: 1502 Rating: (176) |
Hi Do you have the type from the converter ? It give more than 1 pice. http://www.inor.com/ |
Karl |
|