12/19/2017 6:15 AM | |
Posts: 57 Rating: (0) |
sir we are commissioning new Siemens 6ra80 drive.as per operation manual startup procedure as per Quick commissioning DCM 6RA80Created by:lsierdsmaat: 1/6/2015 11:03 AM (1 Replies).I am not getting acess autorisation parameter p0003.i did the parameterization as per process and p3900 made=3, but after that p0010 no gatting 0.also drive tripping on F60056.please guide the same. |
12/19/2017 6:54 AM | |
Joined: 8/25/2006 Last visit: 5/20/2024 Posts: 2205 Rating: (278) |
r0949 in 6RA80 contains fault value as in 6Ra70. You can also look in r50047[0]. |
12/19/2017 7:10 AM | |
Posts: 57 Rating: (0) |
R 50047 showing 3 |
12/19/2017 7:17 AM | |
Joined: 8/25/2006 Last visit: 5/20/2024 Posts: 2205 Rating: (278) |
3: Rated field current of the motor not set (p50102) |
12/19/2017 7:50 AM | |
Joined: 8/25/2006 Last visit: 5/20/2024 Posts: 2205 Rating: (278) |
List Manual with fault description. Operating Instructions, look for comissioning steps in chapter 8. |
12/19/2017 9:08 AM | |
Posts: 57 Rating: (0) |
Sir i do not having acess to p2000 Please guide |
12/19/2017 9:46 AM | |
Posts: 57 Rating: (0) |
yes sir working from BOP20, not showing access p0003 and p2000. starting from r0000, then showing P0010. |
12/19/2017 9:54 AM | |
Joined: 8/25/2006 Last visit: 5/20/2024 Posts: 2205 Rating: (278) |
Look into Operating Instructions, chapter 9.2.2 how to change drive object and parameters from BOP20. |
12/19/2017 2:15 PM | |
Posts: 57 Rating: (0) |
Thank you sir P2000 set to 1800.drive trial taken.working ok |
12/20/2017 12:10 PM | |
Joined: 8/25/2006 Last visit: 5/20/2024 Posts: 2205 Rating: (278) |
Check p50115. |
12/20/2017 12:28 PM | |
Joined: 8/25/2006 Last visit: 5/20/2024 Posts: 2205 Rating: (278) |
Did you make required optimization runs? p50051=24, 25, 26? |
12/21/2017 6:47 AM | |
Posts: 57 Rating: (0) |
Yes sir.but arm voltage is not increasing above 290 |
Last edited by: Vishal Jakkani at: 12/21/2017 6:48:11 AM |
|
12/29/2017 9:12 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello Vishal Jakkani, Is your problem solved? If not, please check if the drive controls the motor in current control mode, not allowing armature voltage to rise. Please set P50171 & P50172 = 100. Please set P2002 = 21 & check. HTH. |
1/20/2018 4:15 AM | |
Posts: 57 Rating: (0) |
Sir sorry for the delay during trail Drive incoming fuse where blown and Y-phase thyristor Found short. reason not identified.we are not having spare drive. |
1/20/2018 4:51 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
What is the present status? Is machine working or not? Is your problem solved or not? |
1/23/2018 10:28 AM | |
Posts: 57 Rating: (0) |
no sir problem not solved. machine is not working, running on single scrap winder, as we are not having spare drive. |
Follow us on