Hello rabindra_rabi, Since your PT ratio is 33KV/110 volt, relay resets when pick up voltage reaches to set volt i.e. 110V. So the relay function & parameter setting are correct. I would suggest you to check why HT 33KV voltage increases (normally it should not be more than 34.5 KV) up to 36.3 KV (equals to 125 Volt) ? |