Hi Everyone, I have the same problem with my WinCC project, i have a 9 client, where on one of them the project is activete very fast and smooth, but on the other client activating process stuckes on loading script server for a few minutes. Version WinCC is 7.5 with SP2 Server is work on Windows Server 2019 Clients is work on Windows 10. Can you help my to find some solution of this problem? Best Regards, Tomek ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/16/2021 14:17:15New subject after splitting |
|
8/17/2021 1:32 PM | |
Joined: 10/10/2014 Last visit: 8/28/2024 Posts: 1725 Rating: (210) |
Hi TomekB90, Activate the tool apdiag and check the messages when you start the project. Check also it the Windows 10 version is tested and released with WinCC V7.5 SP2 Not all of the Windows 10 Version arr released wit WinCC V7.5 SP2 Compatibility Tool for Automation and Drive Technology https://support.industry.siemens.com/cs/ww/en/view/64847781 I recommend also install the Update 4 from WinCC V7.5 sp2 on all Clients and Server Updates for WinCC V7.5 SP2 and WinCC V7.5 SP2 ASIA https://support.industry.siemens.com/cs/de/en/view/109793460 Best regards schufri |