2/17/2010 10:27 AM | |
Posts: 20 Rating: (0) |
r002=29.93 r003=220 r004=685 r005=25.6 r007=46 Measured value (with multimeter) = Phase to phase motor voltage=260V Phase to ground=246V |
2/17/2010 12:16 PM | |
Posts: 20 Rating: (0) |
ELIN motor typ:MKH-745 B06 FWB rpm:1030 6 pole torque:6490Nm |
2/18/2010 11:10 AM | |
Joined: 7/8/2009 Last visit: 7/26/2023 Posts: 1974 Rating: (477) |
Hi Sorry for delay in reply.. I was little busy.. Now as per your data, At 30 Hz freq your torque is 6490*0.46 = 2985.4 Speed is 1030*30/60 = 515 -- I think your motor rated freq is 60 Hz Now for Power calculation, see attached document, P = M * n = 2985.4 * 515 = 154 KW I hope you are clear now.... Regards, Devesh Vithani AttachmentEquations - Formulaes.pdf (278 Downloads) |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|
This contribution was helpful to1 thankful Users |
2/18/2010 1:10 PM | |
Posts: 20 Rating: (0) |
Thanks your answer So, what about parameter of r005? You calculated power 154kW. How can we find 154kW using r005? best regards.. |