9/9/2019 9:34 PM | |
Joined: 2/1/2010 Last visit: 5/24/2024 Posts: 143 Rating: (68) |
You can change the message properties of any block in the library by (make sure you do this in your master data library, not the APL library directly): In your use case, I assume you are going to going to make this setting on one of the external message inputs? Otherwise it doesn't make much sense because then all your alarms for MonDiL will be that class after you sync, unless that's what you really want. |
Last edited by: RVS.wick at: 09/09/2019 21:35:47If my post helped you, please rate. Thanks. |
9/9/2019 11:03 PM | |
If you go to the "With Acknowledgement" column you have to deselect the check box. Then alarm classes without acknowledgement are available for selection in the drop down. |