Mich, 1. Bring the machine in a safe state or start state. 2. Compare the existing offline code with online code to make sure there is no difference 3. Backup the online plc code completely,noton the offline code but in a seperate fie. This way you are saving all the DBs with their parameters. Regard, Behnam www.sigmaprocess.ca/blog |
9/17/2010 6:37 AM | |
Posts: 2348 Rating: (264) |
Also it's better to ensure, that total power consimption doesn't exceed power supply current. Also please mention restrictions on maximum number of modules |