9/8/2010 9:41 PM | |
Posts: 11 Rating: (0) |
Oh, thanks a lot!! Now it works! There was a failure in the definition of the global area pointer. The PLC-tag was not defined correct. |
9/8/2010 10:06 PM | |
Joined: 9/23/2005 Last visit: 9/9/2024 Posts: 4347 Rating: (1442)
|
Hi, I'm happy, that all works now. |
Denilson Pegaia |
|
7/31/2013 6:14 AM | |
Posts: 84 Rating: (20) |
Hi Bryn, I too face the same problem, how you made the solution. I didnt understand clearly what MrPegaiamentioned. "try to change the attribute of the varible DB time sync time sistem Read of the HMI from "cyclic in operation" to "cyclick continous" and tell us if it goes better..." I have changed the "time_system_READ" tag to Cyclic continuous. but still the same, HMI time sync with PLC but alarms with year 2004. Please explain me how to do this. Thank you.
|
Last edited by: subin at: 7/31/2013 6:32 AM |
|
7/31/2013 9:16 AM | |
Joined: 4/24/2006 Last visit: 9/9/2024 Posts: 8735 Rating: (1167) |
Hello subin, It's about the Area Pointer "Date/Time" Best regards, Wizard |
8/15/2013 8:11 AM | |
Posts: 84 Rating: (20) |
ThanksKahlnWizard, It works now. |
This contribution was helpful to1 thankful Users |
2/10/2014 11:48 AM | |
Posts: 340 Rating: (6) |
new question is splittet towrong date/time in alarms, IM 151-8 PN/DP and KTP400 |