5/6/2009 5:14 PM | |
Joined: 5/28/2008 Last visit: 11/6/2024 Posts: 4516 Rating: (839) |
Hello, Please check that cables of each transducer is shielded and connected to the ground. Regards |
Ayman Elotaify |
|
5/6/2009 5:17 PM | |
Joined: 12/5/2006 Last visit: 2/6/2024 Posts: 73 Rating: (4) |
Hi KJLRWW, a very common issue with Analog variation is the proper connection of the M terminal orgrounding interferences. I found this usefull link related to your problem it might help you fix your issue. http://support.automation.siemens.com/WW/view/en/2415890 Regards |
5/7/2009 4:17 PM | |
Joined: 12/5/2006 Last visit: 2/6/2024 Posts: 73 Rating: (4) |
To confirm the answer to your Question KJLRWW whether you should be grounding the return of your sensor or not. If you look at the S7 200 manual http://support.automation.siemens.com/WW/view/en/1109582 If you go in the appendix Page 428/554 the drawing for the 0CH22 shows that the M is grounded, now why is it not the case with your other systems now this requires a bit more analysis on site and studying the wiring conditions of each system individually also the components installed and their revisions. Regards |
5/11/2009 7:34 AM | |
Posts: 5 Rating: (0) |
Thanks All. I was on site yesterday and it turns out the PLC was powered by a temp UPS supply. We connected the standard VT supply and the problem was sorted... |
5/12/2009 6:11 AM | |
Posts: 217 Rating: (52) |
Hello, Nice to hear every thing is OK. And many thanks for your feedback, which is very valuable to us. Best regards. |