Dear pmsilva, Here is a link to manual: http://support.automation.siemens.com/WW/view/en/8859629 See chapter 6.7 page 285 (technical data) Here you will see that changing Integration Time or Interference frequency suppression will result in desired resolution bits. An integration time of 100ms will have resolution of 14 bits. Best regards, Wizard |
1/28/2009 2:29 PM | |
Posts: 3 Rating: (0) |
Thanks to the usefull help. PSilva |
1/28/2009 5:05 PM | |
Joined: 4/24/2006 Last visit: 11/11/2024 Posts: 8768 Rating: (1170) |
You are welcome Greetings Wizard |