8/19/2011 12:39 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715) |
Hello, |
Last edited by: Marcjan at: 8/19/2011 12:41 PMProblem solved? |
|
This contribution was helpful to1 thankful Users |
8/21/2011 12:00 AM | |
Joined: 10/7/2005 Last visit: 9/19/2024 Posts: 3021 Rating: (1054)
|
Hello Tom66 Siemens uses the terms "2-wire" (forpassive) and"4-wire" (foractive) instead,the differences in connections can be found in the manual too and the 7KF02 can definetely be used for either as well as PT100's. You may also find the following FAQ's helpful (note too the additional links in the top of each page): How should you connect and wire measuring transducers and M connections taking the example of the SM331 (6ES7331-7KF02-0AB0 and 6ES7331-1KF01-0AB0)? What measures do you need to take for error-free operation of the analog input modules SM331 (6ES7331-7KF02-0AB0 and 6ES7331-7KB02-0AB0)? I hope this helps |
Cheers |
|
8/22/2011 3:59 PM | |
Joined: 10/7/2005 Last visit: 9/19/2024 Posts: 3021 Rating: (1054)
|
Hello Tom66 you are correct, the 1KF02 has no range modules and is NOT capable to power 2 wire (or passive) Instruments(external loop power supply is required if you want to connect these). I suppose I also need to apologise for not reading your post carefully enough (you were talking about the 1KF02 and I replied with a reference to the7KF02). |
Cheers |
|