2/1/2023 3:56 PM | |
Joined: 8/12/2021 Last visit: 5/17/2024 Posts: 308 Rating: (29) |
Hi Joanna.S! If I'm not wrong, you just need to not configure the output you are not going to use. Have a look at this manual.
|
If this Information really helps, you could use the Rate function |
|
2/1/2023 8:22 PM | |
Joined: 3/28/2015 Last visit: 5/15/2024 Posts: 721 Rating: (213) |
Hello, 1-In the H.W configuration of Step7,Deactivate the unused group. 2-If one input of the group is not used,you can Deactivate the Group diagnostics for this group or connect a resistor (1.5K to 3K ohm) between the unused input terminals. |