10/31/2022 6:26 AM | |
Joined: 7/30/2012 Last visit: 5/12/2024 Posts: 335 Rating: (12) |
Hello, Have you seen this? for controlling it possible with analog signal but for feedback its required encoder signals https://support.industry.siemens.com/cs/ww/en/view/109741575 |
Last edited by: @KB@ at: 10/31/2022 09:47:38Last edited by: Jen_Moderator at: 11/03/2022 13:01:57Link optimized |
|
This contribution was helpful to1 thankful Users |
11/3/2022 9:18 AM | |
Joined: 7/25/2017 Last visit: 5/22/2024 Posts: 297 Rating: (44) |
Good day Fabio Locatelli Yes you can do it; that is one of the advantages of S7 technology objects; they're hardware agnostic. Specify DB for the encoder type. Then you emulate the required encoder signals by writing to the DB. There is a guide to this somewhere. However, you need to tune the axis according to the limitations of this encoder - in terms of mechanical stiffness and electrical noise.
AttachmentPosAxis_LinearEncoder.zip (574 Downloads) |
This contribution was helpful to1 thankful Users |