2/4/2018 8:54 AM | |
Posts: 6 Rating: (0) |
Here,s the programm
AttachmentAnalogeInput.zip (211 Downloads) |
2/4/2018 9:49 AM | |
Posts: 6 Rating: (0) |
I placed the wrong file as programm. this is the right one . when i simulate the network input, the value change in my screen. i show a picture of that AttachmentAnalogeInput.zip (182 Downloads) |
2/4/2018 9:57 AM | |
Posts: 6 Rating: (0) |
in the picture you can see that the value is 114 thats coming von a app of my telephone. |
Last edited by: Rdeleeuw at: 2/4/2018 9:58:02 AM |
|
2/4/2018 10:37 AM | |
Posts: 6 Rating: (0) |
I have a app named HMI MULTI LOGO, there ther you can set an analoge value ( %VW1) in network 1 i used a analoge network input en connect that directly on a analoge output thats works ok. it only works when i used adress VW2 , starnge but true
AttachmentAnalogeInput1.zip (176 Downloads) |
2/4/2018 10:58 AM | |
Joined: 12/18/2014 Last visit: 10/5/2024 Posts: 33882 Rating: (4214)
|
I have now set up the transmission of two words in the connection list, VW0 and VW2. For NAI1 you have to write in the app in %VW0, for NAI2 you have to write in the app in %VW21. Edit: I have just found the manual for the app in the WWW. % VW0 in the app corresponds to the LOGO! VW0 AttachmentAnalogeInput2.zip (209 Downloads) |
Last edited by: ixo65 at: 2/4/2018 11:19:41 AM |
|