6/4/2014 8:18 PM | |
Joined: 10/3/2010 Last visit: 9/30/2024 Posts: 1562 Rating: (192) |
If no other solution, try using reset_wincc.vbs instead. It doesn't happen daily? |
B r g d s , |
|
6/4/2014 10:52 PM | |
Joined: 9/3/2008 Last visit: 10/11/2024 Posts: 928 Rating: (162) |
If the issue is still about shutting down WinCC gracefully using the UPS, then use the following FAQ: How do you safely terminate WinCC by means of an external application? http://support.automation.siemens.com/WW/view/en/89257244 You do not need internal tags. |
Michael |
|
This contribution was helpful to1 thankful Users |
6/5/2014 8:21 AM | |
Joined: 10/3/2010 Last visit: 9/30/2024 Posts: 1562 Rating: (192) |
TomazO, Reset_WinCC.vbs is not "killing", it's stopping all WinCC processes and services, without warnings. If UPS Needs to Shutdown, it's much safer to force Reset_WinCC and shutdown Windows in a safe way than to have a sudden powerloss on a running Windows & WinCC. If you can't live with the above solution, you'll need to make a Support Request for an change request to the c-script. |
Last edited by: SteBo at: 6/5/2014 8:32 AMB r g d s , |
|
8/8/2014 12:59 PM | |
Joined: 9/1/2005 Last visit: 10/9/2024 Posts: 4109 Rating: (195) |
new question published by CerTMis split to a seperate thread with the subject APC UPS and redundant WinCC server shutdown. Best regards CS Moderator |