5/28/2014 8:45 AM | |
Joined: 3/21/2006 Last visit: 7/26/2024 Posts: 10228 Rating: (1181) |
With PM240 300 m is not valid. |
5/28/2014 9:03 AM | |
Joined: 5/29/2013 Last visit: 5/16/2022 Posts: 6 Rating: (0) |
if when two motor chokes? |
5/28/2014 9:25 AM | |
Joined: 5/28/2008 Last visit: 8/27/2024 Posts: 4515 Rating: (838) |
Hello, Max. Cable length depends on fram size and / or power in according to table of this link: SINAMICS G120 Power Module PM240--- Please see section 4.2 Hope this helps. |
Ayman Elotaify |
|
This contribution was helpful to1 thankful Users |
5/29/2014 1:18 PM | |
Posts: 235 Rating: (52) |
Dear Belvmen, Thanx for the question. I am also facing such aproblem in one of the my project,in which the distance between Drive(G120,CU240E‐2 DP E‐TYPE) and Motor is more than 800 meter.Hence we ask to the siemens vendor as well expert too.Unfortunately this is not possible with siemens drive(sinewave filter / output choke)(note more than 325 meter).But reference of another german based company(SCHAFFNER) which have made such a sine wave filter to use upto 2000meter length. So we are finaly going through this (SCHAFFNER) make. For more detail please find the attachement for the same. AttachmentSchaffner Output Filter.pdf (768 Downloads) |
This contribution was helpful to1 thankful Users |
5/30/2014 5:02 AM | |
Posts: 4 Rating: (0) |
Please, me too keep in mind cable and laying cost for 2 kms of cables. |
4/22/2015 2:15 PM | |
Joined: 8/7/2013 Last visit: 8/13/2024 Posts: 90 Rating: (1) |
dear sir I am also facing this problem my details are as below
SYSTEM: CU: 240E-2 DP Ver. A04-4.60 PM: 240 Version J FAULT: F30002 (DC LINK OVERVOLTAGE) APPLICATION: PUMP VFD TO MOTOR DISTANCE: 750+ Meter OUTPUT SINEWAVE FILTER: 1 Nos SCHAFFNER: Nominal OP Voltage 3*500VAC; Motor freq 0 to 70 Hz Rated current 4.5 to 2000 Amps Max Cable length: up to 2000 Meter PROBLEM: We have done commissioning total 26 Nos of VFD (37Kw*18No);(30Kw*8Nos); Here total 6 Nos of VFD are tripping on dc link overvoltage immediately when on command is given; all the VFDs are of same application and parameterization is same for all of them; other VFDs are working fine but only these 6 VFDs are tripping. TRIALS TAKEN: To rule out possibility of faulty output filter or motor and power cables we have interchanged the working VFDs with this tripping VFDs; here no tripping was observed Changed Control Units of working VFDs with Tripping VFDs, still VFDs were tripping. OBSERVATION: During trials we have observed that when the supply voltage is around 390V drives are not tripping; setting in P210 (Input supply voltage) =400V; tripping occurs when the supply voltage is 400-410V(P210=400V). Trial taken with same value set as supply voltage in p210 i.e. if supply voltage is 410 set p210=410 after this setting also tripping is present. Attachmentdetails.pdf (582 Downloads) |
Last edited by: hsnaik at: 4/27/2015 2:47:13 PMLast edited by: hsnaik at: 4/28/2015 2:34:22 PM |
|
Follow us on