5/30/2014 11:08 AM |
|
Posts: 17 Rating: (4) |
Dear PISCEAN 2010, For HT side cable 16 sqmm XLPE cable is required,but i dint think wolvarine need this cable because he is asking for trafo to LT panel only. And for LT side cable as per current rating 695A, it should be a 400 sq.mm * 2 run cable is minimum required to carry this current. for more details please follow thislink
|
5/30/2014 11:39 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, The attached catalogue is of LT cable. In case of HT side, since cable is laid in ducts/underground & in case of fault current & consideringline impedence, the cable size is selected. (PLEASE NOTE). THat is how 95 sq mm cable (ALUMINIUM CONDUCTOR) is recomended. On LT side 240 sq mm XLPE insulated 2 runs are recomended. i.e. 399*2 = 798A HTH. |
5/31/2014 2:29 PM |
|
Posts: 17 Rating: (4) |
thanx for this post |