10/16/2017 7:51 PM | |
Posts: 4 Rating:
|
Need Help! Can anyone please tell me which memory of a PLC decides Number of supported DI/O or AI/O. I have S71200 CPU 1211 and 1212 (DC DC DC). And how to calculate Expansion Modules to Input/Output. For example: Total expansion modules to total DIO. Total expansion modules to total AI/O. |
10/17/2017 1:05 AM | |
Joined: 7/2/2016 Last visit: 6/18/2024 Posts: 120 Rating:
|
Hello Khanzada0786, the number max of I/O per CPU in 1200 line are: CPU - MAX DIGITAL - MAX ANALOG 1211C - 18 - 4 1212C - 86 - 20 1214C - 288 - 68 1215C - 288 - 68 1217C - 288 - 68 attached CPU specs compare Best Regards, DINIZ --- if it was helpful please rate the post.
AttachmentS7-1200 CPUs COMPARE.pdf (443 Downloads) |
hope this help, if it was helpful please rate the post! |
|
This contribution was helpful to
2 thankful Users |
10/17/2017 10:50 AM | |
Posts: 4 Rating:
|
Hi Diniz, Thanks for the response. But my question still remains. Which type of memory decides total number of inputs and outputs? 1212C supports two expansion modules: If i connect all DI/O modules. OR If i connect all AI/O modules. Then i need total number of input/output calculation? |
10/17/2017 11:25 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi Khanzada, no one of them. It´s ment all together. The total number of Inputs and outputs is not depending on digital or analogue I/O´s. The S7-1212 has an Address-area of 1 kbyte. That means addresses in the central and decentral periphery. It doesn´t matter if your expansion-modules are analogue or digital. hope this helps, regards, |
FCK WAR! |
|
10/17/2017 3:35 PM | |
Joined: 7/2/2016 Last visit: 6/18/2024 Posts: 120 Rating:
|
Dear Khanzada0786, the memory is not the unique limitation for physical IO quantity of the CPU, for example you can put a MMC (32GB) on 1212C but you still be limited two IO modules. at TIA Selection Tool (online or donwnload) you can configure your rack and see the limitation very clear. below the link is a very good tool and you will have more benefits like complete bill of materials (MLFB) check all accessories. lets try it... --- BR DINIZ if it was helpful, please rate the post! |
hope this help, if it was helpful please rate the post! |
|
10/17/2017 8:14 PM | |
Posts: 4 Rating:
|
Hi, Thanks for the response. 1Kb=8000 bit So it mean that i can connect 8000 DI/O to CPU 1212C. 1Kb=1024 bytes and 512 AI/O.Because one analog input or output uses 2 bytes. But there is no such expansion module.Am I right? regards, |
10/17/2017 10:05 PM | |
Joined: 7/2/2016 Last visit: 6/18/2024 Posts: 120 Rating:
|
Dear Khanzada0786, The memory of CPU is used to storage the user program and to processing the operational system because it math is a little bit different. those values what you mentioned are a high density of phisical I/O and for that quantity you probably need a S7-400 CPU... — BR DINIZ if it was helpful please rate this post. |
hope this help, if it was helpful please rate the post! |
|
10/17/2017 10:42 PM | |
Posts: 103 Rating:
|
The allocation of the memory for the S7-1200 is fixed in size and type. The linking to IO comes with addressing space made available. Regardless of this, Siemens has fixed the count of expansions that you can use. For all you have the 3 communication modules to the left and the expansion card that pushes onto the main CPU. The expansions to the right of the CPU is fixed according to the PLC you choose. That is more to do with the power made available on the internal bus, but it is most to do with the limitation that Siemens put there. The CPU1212 handles two cards to the right. Nothing more. You have to ensure you have the maximum density cards you can find as there is no way around the set rule of two cards. Better news is that communication driven IO can be used. Even linking to another S7-1200 is made more-or-less easy. The less expensive way remains to get a CPU1214. The communication linked devices make use of the extra addressing space which is not used by the extension cards. As you have mentioned, that is more than you can use for S7-1200 type projects.
|
Last edited by: CJ4 at: 10/17/2017 10:44:57 PMLast edited by: CJ4 at: 10/17/2017 10:47:24 PM |
|
10/18/2017 11:52 PM | |
Joined: 7/7/2010 Last visit: 4/15/2025 Posts: 15808 Rating:
|
You will run out of processing power or program working memory long before you run out of space for the I/O on a s7-1200 project - once you consider remote or distributed I/O as still part of the I/O space allocation.
|
science guy |
|
10/19/2017 1:20 PM | |
Posts: 4 Rating:
|
Thanks for the response. The problem is that I have an S7-1200 CPU 1212C which allows only two expansion modules. Now if I use two analog modules each containing 8 channels, which is the maximum number of channel currently available in a Siemens S71200 AIO expansion module.i.e (6ES7231-4HF32-0XB0). This will give me a total AIO count as follows, From expansion modules: 16 channels Built in : 2 channels Signal board expansion :1 channel i.e(6ES7231-4HA30-0XB0) Total AIO=16+2+1=19 Channels Is this configuration correct? This arrangement will not have any negative effect on the processing power of the CPU? regards, |