2/27/2015 6:17 AM | |
Posts: 153 Rating: (8) |
1200 does not have 5V differential driver outputs. I would suggest that you read this https://support.industry.siemens.com/cs/#document/77467940?lc=en-US and do a bit more homework. The V90 and the J4 are nearly functionally identical. |
Last edited by: casajr at: 2/27/2015 6:23:50 AM |
|
2/27/2015 6:36 AM | |
Posts: 17 Rating: (1) |
casajr, I also use FX3 normally.... But, according to application example of CPU1217C and V90, 1.5V differential output on CPU1217C connects to 5V differential pulse train input on V90. Is J4's 5V differential line driver is different with 5V differential pulse train input on V90? Attachment1.5V differential output.pdf (580 Downloads) |
Last edited by: Yusukey at: 2/27/2015 6:41:08 AM |
|
3/2/2015 6:34 AM | |
Posts: 153 Rating: (8) |
Mitsubishi does not document the interface, so who knows? Try it and see. If not, use the 24V inputs. |
This contribution was helpful to1 thankful Users |
2/23/2016 2:55 AM | |
Joined: 9/3/2012 Last visit: 5/6/2024 Posts: 56 Rating: (0) |
Hi,
|