Hi, Can I communicate to modscan using PLCSIM advance and MB_server block within s71500 plc. |
6/28/2021 3:57 PM | |
Joined: 4/28/2015 Last visit: 2/7/2024 Posts: 10533 Rating: (820) |
Hello, if we talk about PLCSIM_Advanced then yes, with also PC app. |
With best regards... |
|
6/30/2021 6:56 AM | |
Posts: 7 Rating: (0) |
Hello Duris-I, Thank you for your reply, I have configured and checked the same with S71500 Configured Project with PLCSIM_Advancev3.0 without the physical PLC.please go through the images file which I have attached and let me know where I'm lagging. warm regards sadhguru Attachments71500.pdf (181 Downloads) |
7/6/2021 10:49 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
hi sadhguru, Why did you set the Disconnect input to "1"? Is it really neccessary to explain this parameter? If the parameter is not set, MB_Server waits for a client.But the client needs to actively establish this connection. Also check the block for errors.See this FAQ, how it works: How do you evaluate the status of system blocks in STEP 7 (TIA Portal)?hope this helps, regards, |
Last edited by: mopS04 at: 07/06/2021 10:50:25FCK WAR! |
|
This contribution was helpful to1 thankful Users |
7/7/2021 7:26 AM | |
Posts: 7 Rating: (0) |
Dear Mop, I heartfully thank you for your response and I will go through and check where I have did a mistake with your shared reference.. warm regards srikanth |