12/27/2021 1:05 PM | |
Joined: 4/28/2015 Last visit: 9/9/2024 Posts: 3345 Rating: (379)
|
Hi, I haven't done this before via 4G, but I think in theory this should work. The first requirement is to connect via the 4G network from remote. Do you already have a solution for this? Probably you need a VPN service or a public IP from your provider. The next step is enabling IP forwarding. This enables the possibilty to connect from the 4G network to the network on eno1 or eno2. In your remote PC you need to set a gateway (IP address of the 4G network). Then you should be able to access your PLC connected to eno1 or eno2 of the IOT2050. To access the underlaid components, such as drives, you need to enable IP forwarding in the PLC settings (possible from FW 2.8 of S7-1500) and likely some more gateway settings in the PLC interface. Best regards! |